    Needing to know what the normal is out there.
    I was taught that when installing a cut-out the line side was the top and the load side was the bottom and that was the way you better build it.
    Anytime you had a tap coming off of the main line, the tap conductor was installed below the main line conductor.
    Also in a pad mount unit the line side cable plugged into the top and the load side cable into the bottom (In high-out low theory)
    A conductor that is used a jumper with a hot line clamp you always have it so that when the clamp is removed with a stick the jumper becomes de-energized.

    Tell me how you guys build things and maybe I am going to have adjust my thinking.

  2. #2

    Default

    Cutouts: Don't assume that the lowside is the load side when you're dealing with underground risers.These are potential traps if they are feeding up the pole.Always follow safe work practices, Identify,Isolate,Test,And Ground.

  3. #3

    Default thats right

    never assume,,,,,,sometimes the overhead is feed from underground ,,,the top of the cutout ,,should be the feed,,it often looks wrong to some lineman ,so they make it the ( normal way),,no matter what,,,,,,,,test it before you touch it ,,period,,,,,,,scammy

  4. #4
    Join Date
    Jul 2003
    Location
    Virginia, USA
    Posts
    549

    Talking conventions

    Electriceel, you were taught the same way I was. HOWEVER in these days of pushing systems to the limit and system improvement jobs always behind new construction more and more lines get switched and feeds changed. So while it may have been built with feed on top and tap below that is no guanantee it still is now. The only safe thing to do is treat it as hot until you isolate - test - and ground.

  5. #5

    Talking Yes

    Quote Originally Posted by Electriceel View Post
    Needing to know what the normal is out there.
    I was taught that when installing a cut-out the line side was the top and the load side was the bottom and that was the way you better build it.
    Anytime you had a tap coming off of the main line, the tap conductor was installed below the main line conductor.
    Also in a pad mount unit the line side cable plugged into the top and the load side cable into the bottom (In high-out low theory)
    A conductor that is used a jumper with a hot line clamp you always have it so that when the clamp is removed with a stick the jumper becomes de-energized.

    Tell me how you guys build things and maybe I am going to have adjust my thinking.
    That's the way it should be. But there's just some times you have to deviate from the norm when you build something. Look things over before you work, tailboards, never never assume. Which you ass.

  6. #6
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    with loop feed systems it would not be practical to have the so called incoming on the top. You have to assume both sides of a switch are alive untill you test & ground.

  7. #7
    Join Date
    May 2005
    Location
    Baton Rouge ,La
    Posts
    992

    Default Thats the way

    I was taught also. But as stated you can't always assume every one was done that way.

    Koga

  8. #8

    Default

    Thanks guys. I should have clarified myself as to overhead construction.
    Agreed never assume anything, we all know what that word means.

  9. #9
    Join Date
    Oct 2006
    Location
    South East Texas
    Posts
    3,278

    Default source/load

    If its a deadblade switch either side can be the line or load however if its a fused disconnect only the top side should be used for the source side.

  10. #10
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    Featured Sponsorr

    Again on a loop system O.H. or U.G. fused or solid switches it does not matter as the in & out can change. On a radial yes the line is on the top & the load is on the bottom or on inline the blade is on the load side so that when open the blade is isolated.