Thread: 1ph pole top reclosers(exploding)

  1. #1
    Join Date
    Dec 2009
    Posts
    3

    Exclamation 1ph pole top reclosers(exploding)

    Featured Sponsor

    Hey brothers,just curious if anyone out there is having new oil switches blowing up when they are energized.I'm looking for a possible trend here.I know of 2 on my system recently & 1 of them put me in the burn center for a short stay & home for a while.Please reply to this thread or e-mail me [email protected] .Thanks &Stay Safe!!!

  2. #2
    Join Date
    Jul 2005
    Posts
    401

    Default Explosion

    I have had it happen to me. I know of others that have too. We used to have a regular maintenance schedule with these bombs. They quit that 25 years ago. We used to take them down bring to shop and overhaul them. This included the reclosures on cap banks also. Like a lot of other things the maintenance is not done anymore. You just replace things when they fail. I can't speak for other utilities but thats where we are at. I would think with the lack of people its the same all over. Anything will fail sooner if not maintained but no one seems to care anymore. Like I mentioned its replace at failure.

  3. #3
    Join Date
    Nov 2007
    Location
    Northeast PA
    Posts
    30

    Default Ticking time bombs

    Our company had a preventive maintenance program to open up, change the oil, and replace any damaged pieces inside these little time bombs. Our substation guys would go out with a line crew take them down rebuild them and putem back up at least once a year! This pm. practice is gone now with all recloser and cap banks as was once done. We have had a practice for the last ten years in our district in PA to close all transformers,reclosers and/or cap banks from the ground with an extendo stick for obvious safety reasons.......no prev.maint. any more....buying cheaper 2nd rate transformers and reclosers!.......Hell weve put up new reclosers and the first time they operate in a storm they dont close back in!JUNK
    Beware of the TICKING TIME BOMBS and protect our own with all the cutbacks and not become a statistic!

  4. #4
    Join Date
    Jul 2003
    Location
    Virginia, USA
    Posts
    489

    Post Maintenance

    Over the last 15 years our Coop has slowly replaced all of our OCR's with vacumn OCR's. This has changed the maintenance cycle considerably versus the non-vacumn. We do still read all OCR's once a year and base changeouts on actual number of operations. Even with this though we have had 2 in the last ten years go "ballistic" on us. Our policy is you NEVER close an OCR from hooks, only an extendo or with a finger stick from a bucket offset to the side. I heard from some Dominion people that they had a real problem for a while with ABB 34.5kv three phase reclosers about three years ago. I have not heard of any recently, don't know if it was a manufacturers defect or what. I do know they had one in Wialliamsburg, one in Isle of Wight, and one in Southampton all blow a bushing to pieces. The same serviceman closed two out of the three and was getting REAL nervous around them.

  5. #5
    Join Date
    Dec 2009
    Posts
    3

    Default

    Quote Originally Posted by thrasher View Post
    Over the last 15 years our Coop has slowly replaced all of our OCR's with vacumn OCR's. This has changed the maintenance cycle considerably versus the non-vacumn. We do still read all OCR's once a year and base changeouts on actual number of operations. Even with this though we have had 2 in the last ten years go "ballistic" on us. Our policy is you NEVER close an OCR from hooks, only an extendo or with a finger stick from a bucket offset to the side. I heard from some Dominion people that they had a real problem for a while with ABB 34.5kv three phase reclosers about three years ago. I have not heard of any recently, don't know if it was a manufacturers defect or what. I do know they had one in Wialliamsburg, one in Isle of Wight, and one in Southampton all blow a bushing to pieces. The same serviceman closed two out of the three and was getting REAL nervous around them.
    Thanks for the info.2 incidents lately & the one I was involved in were brand new & identical.I have since learned that water & rust were found in both.Im starting to suspect manufacturer defect.

  6. #6
    Join Date
    Sep 2004
    Location
    Heart of Virginia, USA
    Posts
    764

    Default

    interesting... who's the manufacturer... and where were they made>???

    ohh and are they ship dry then oil capped at your shop?

    or are they shiped "ready to go" and just put on the line?

    if so are they inspected by your transformer/breaker shop prior?

    just wondering....

    this is the kinda thing that could save a brother...

    for what it's worth...

    Edge

  7. #7
    Join Date
    Dec 2009
    Posts
    3

    Default

    Featured Sponsor

    The ocr came filled & ready to go.You guys be careful.