05-30-2013, 05:51 PM
Do you all ground your pole mounted distribution capacitor bank brackets???

reppy007
05-30-2013, 08:53 PM
Its been a long time since Ive seen that done,when the brackets were steel it was very common....now Ill assume its up to the crew involved.....with a shortage of men and more work placed on them,some guys aint going to take time to ground the racks.

Lineman North Florida
05-31-2013, 06:17 AM
We ground the tanks and the brackets, but we float the high side, this is where you will get into the difference on how different one companys specs are verses another.:D

Rob
05-31-2013, 10:51 AM
The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here

Orgnizdlbr
05-31-2013, 11:48 AM
The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here

Same with us......

lewy
06-01-2013, 06:51 AM
The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here

Your down ground is connected to your system neutral? If not it should be.

PHASE2PHASE
06-18-2013, 01:21 PM
Every ground in PE Florida is tied to neutral