How many of you have or havent worked on an urd loop that was fed off the circuit which was energized 19.9 and was stepped down to 7200 by stepdowns all on one pole,does it pose any problems as far as your concerned.....pros and cons ?
T-Man
11-12-2013, 06:50 PM
We converted to 14.4/24.9 and when the main line went past an 8 kv URD subdivision we stepped down out on the main line and fed the URD from there. The problem came when we only fed half of the subdivision from each voltage. The bridging point in the URD would be out of phase and if you closed there you blew fuses on the risers if you were lucky. So we marked that bridging point in the field and on the operating maps in the control center.
reppy007
11-12-2013, 07:24 PM
Thats a new one on me big T.....Two different voltages on the same loop.....wonder how common that is?
reppy007
11-12-2013, 07:38 PM
Its not too common here ....but the one's Im talking about is like 6 poles in a row that are paralleled with 167kva stepdowns....so when the loop goes out you have to figure if one is bad,your usually going to have to change the limiter and find the trouble on the loop itself.Now if you happen to have two faults on the loop you feel like you just won the lotto :D
Pootnaigle
11-12-2013, 10:21 PM
U MM WEHADDA13 TO 34.5 STEP UP RUNNIN A SMALL ADDITION overhead n hada major prollem with guys that knew the area to be 13 n when changin a pot they wud use one wound for 13 n it didnt werk too good
reppy007
11-12-2013, 10:41 PM
U MM WEHADDA13 TO 34.5 STEP UP RUNNIN A SMALL ADDITION overhead n hada major prollem with guys that knew the area to be 13 n when changin a pot they wud use one wound for 13 n it didnt werk too good
Funny that lineman grow big balls when the voltage is steped down and those same balls srink when the voltage is stepped up.
T-Man
11-13-2013, 07:06 AM
Thats a new one on me big T.....Two different voltages on the same loop.....wonder how common that is?
It's not common reppy, but during the cut over to the higher voltage and the distance on the main line between down feed risers into the existing urd loop, once in a while one riser gets cut over a day or two before the other and the bridging point has the same phase and voltage but different angular displacement and can not be closed. So when the time comes there is a short outage set up where the old riser is opened, load dropped and the bridging point is closed. Then, when the last riser is cut over to the new voltage with step down , they can phase and close in the open bridging point now at the first tub off the riser and then open the original bridging point and the system is being fed as before. They correct the maps and signage that indicate irregular phase displacement in the field location.
reppy007
11-13-2013, 11:03 AM
More than once ,usually after a flood Ive been behind lineman that would shoot the fuse feeding a step-down when theres transformers in a low area down the street....now the problem was that these transformers happened to be livefronts.....underwater and all....and many of times that would cause the transformers to be damaged on the inside,as far as Im concerned stepdowns are more sensitive than other transformers.This happened twice in an area that I was sent to many of years ago,twice in the same hour....I wondered,where do they get these guys ....did they actually think it would hold?
rob8210
11-15-2013, 07:27 PM
I worked at one utility that would build an underground loop then feed it one phase from one end and a different phase from the other end! Same voltage though.
Lineman North Florida
11-15-2013, 09:14 PM
I worked at one utility that would build an underground loop then feed it one phase from one end and a different phase from the other end! Same voltage though.What could possibly be a good reason for them to want do that?
reppy007
11-15-2013, 11:37 PM
Im with ya LNF.....Ive always thought having them both on the same phase was the rule of thumb and not the thumb of rule :D
rob8210
11-16-2013, 07:50 AM
There was no valid reason it just was. It was an unusual place many odd ways of doing things.
trigger
11-18-2013, 11:55 PM
You would be able to swap load if needed. Balancing feeders.
Lineman North Florida
11-19-2013, 06:41 AM
You would be able to swap load if needed. Balancing feeders. In my opinion if that's their reason for having a 2 different phases in an open point transformer, then the potential bad outweighs the good, there are a whole lot of other ways to balance the load on feeders rather than setting somebody up with a dual phase loop.
T-Man
11-19-2013, 07:49 AM
In my opinion if that's their reason for having a 2 different phases in an open point transformer, then the potential bad outweighs the good, there are a whole lot of other ways to balance the load on feeders rather than setting somebody up with a dual phase loop.
I'm with ya on that LNF, too much of a chance to close into opposite phases. Even if you get orders to switch that over, it would have to include a section outage on a clear day to change it over to the other phase. Which sounds simple enough but actually is a lot of horsing around obtaining outages from the customers dropping them then running to the other end closing and picking them up again, checking if everyone is on again (they mess with circuit breakers when the power goes out)
It's not you Rob, it's the system you spoke of.
reppy007
11-19-2013, 08:13 AM
There R other ways to balance a feeders load....why not swap phases feeding overhead laterals....wonder why some places see that practice as being ok....beats me:nightmare:
Having an out of phase condition is never ideal, but there are situations where it is used as a backup for emergency purposes. It should be well taged in the field as well as at your control room.
reppy007
11-19-2013, 12:26 PM
I guess while we are discussing urd I have to ask,and maybe Ive asked before what was the distance of the longest loop you have ever worked on?Here we have several long loops but one that comes to mind was a 12kv loop that was around 5,000 feet long....split with deadfronts,livefronts and a couple of submergeables.