Does anyone know how to wire up 3 50 kva xfmr with a 7200 high side and a 2400 delta low side? Thanks
Pootnaigle
09-07-2012, 07:45 PM
Ummmmmmmmm asuming you have the correctpots it would be bout like any other wye delta transformer bank
rob8210
09-08-2012, 08:12 AM
Why would you want 2400 delta on the low side?
Stormtrooper
09-08-2012, 01:43 PM
Most of the village where I will be going is 2400 delta. They are putting a new diesel generator in and will supply 7200 eventually to the whole village.
rob8210
09-08-2012, 05:30 PM
I tend to agree with Poot, although around here the trend is away from delta secondaries. All new 3 phase banks are built wye-wye and the customer has the secondary neutral available if desired.
rob8210
09-08-2012, 05:33 PM
Of course 3- 50kva cans isn't that much load, why not just simply convert the load to 7200v?
Stormtrooper
09-10-2012, 12:01 AM
Its an Alaskan native village. Most are delta but they are slowly being converted. Like some one else said... I guess it would be wired the same as any other wye delta bank.