    Default Loop VS Radial feed

    Featured Sponsor

    What is the difference between a loop feed and a radial feed?

  2. #2

    Default

    radial is a one way feed......if you have a urd fault underground it cant be switched around....so be ready to dig

  3. #3

    Default

    As Reppy says. In general electrical terms a radial is one line extending out, while a loop is a line that goes out and comes back to the point it's being fed from. The advantage of the loop is that if a fault occurs you can isolate that section on either side of the fault and everything else stays up. That keeps customers happy and takes the pressure off the repair crew.
    Portable defibrillators were first invented to save the lives of linemen. Where's yours?

    www.bigclive.com

  4. #4

    Default

    Im kinda wondering what others call a 3 way feed on a single phase loop....we call it a (x-y-z) and one thing about them....they are fairly unusual....Ive only seen a few here.....many guys would go crazy trying to figure out a urd switching order with 3 terminal poles involved....but my questions would be if anyone has seen more than 3.....another question is how many times have you used one of those stand-offs with 3 bushings...all 3.....never seen those used too often,I even think many were thrown away.

  5. #5
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    Quite common here along with sectionalizers, that is what maps are for.

  6. #6

    Default

    Never seen a 3-way URD feed, seen a regular loop or 2-way with a radial pull-off with either a T-splice or transformer mounted 2-bushing insert. I'm guessing on these 3-way feeds that you would have 2 open loop transformers or 2 opens?

  7. #7

    Default

    Here in CT. they've had what the Co. calls Loop Schemes for 15-20 years, they put a lot of faith in technology and maybe not so much into common sense. Some of the loops tie the same feeder some different feeders, usually 5 reclosers in a typical loop sometimes the engineers get a little fancy and we've had up to 5 reclosers feeding into one piece of wire, it pays to take your time responding to these outage calls just to make sure they've done all their flopping. Usually there are 500 customers between reclosers. We spend a lot of time switching to repair downed conductor going to all the reclosers feeding into the fault and removing taps then going back to ground, tried to get the Co. to make it standard to put disconnect switches on the load side to make this a little quicker and easier but the bean counters said cost to much.

  8. #8

    Default

    I'm thinking that we are possibly talking about 2 different things, up North I have heard them speak of loops talking about overhead, down South when we are talking loop we are generally speaking of underground, when I responded to Reppy's post that's what I took it that he was talking about.

  9. #9

    Default

    Quote Originally Posted by Lineman North Florida View Post
    I'm thinking that we are possibly talking about 2 different things, up North I have heard them speak of loops talking about overhead, down South when we are talking loop we are generally speaking of underground, when I responded to Reppy's post that's what I took it that he was talking about.
    Yea ,me too when i mention loops im talking underground,i should have made it more clearer.Sorry .

  10. #10
    Join Date
    Oct 2006
    Location
    South East Texas
    Posts
    3,278

    Default

    Featured Sponsorr

    ummmm sum of our trunk overhead lines are looped. they have sum kinda smart ocb that can tell where a fault is n opens another ocb on either side of it n then closes a normal open ocb