Results 1 to 7 of 7
  1. Default Cap bank brackets

    Featured Sponsor

    Do you all ground your pole mounted distribution capacitor bank brackets???

  2. #2

    Default

    Its been a long time since Ive seen that done,when the brackets were steel it was very common....now Ill assume its up to the crew involved.....with a shortage of men and more work placed on them,some guys aint going to take time to ground the racks.

  3. #3

    Default

    We ground the tanks and the brackets, but we float the high side, this is where you will get into the difference on how different one companys specs are verses another.

  4. #4
    Join Date
    Jan 2012
    Location
    New York, Long Island
    Posts
    343

    Default We ground

    The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here

  5. #5
    Join Date
    Mar 2003
    Location
    Jersey
    Posts
    2,512
    Blog Entries
    1

    Default

    Quote Originally Posted by Rob View Post
    The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here
    Same with us......
    "It is not the critic who counts:The credit belongs to the man who is actually in the arena" Teddy Roosevelt

  6. #6
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    Quote Originally Posted by Rob View Post
    The brackets are grounded to a down ground (driven ground). The tanks are grounded to system neutral here
    Your down ground is connected to your system neutral? If not it should be.

  7. Default Grounds to neutral

    Featured Sponsorr

    Every ground in PE Florida is tied to neutral