  1. Default pad mount transformers, underground feeders question

    Featured Sponsor

    We have a 5 kv distribution line dead ended on a dip pole. There are three solid blade/porcelain "chocolate box" type disconnects feeding one set of 3 phase undergrounds. There's about a quarter mile of underground feeding three 500 kva pad mounts for various commercial properties.

    A few months back, I got sent out to pull these disconnects so a contractor could work on a service. It was 5 am and pitch dark out. I pull the first one, when I pulled the second, it drew an arc fully open. I remembered some old time telling me if that happens, wave the stick through the arc to kill it. That didn't work and this thing was blazing. Now I can't see sh*t with the ball of fire to get the hot stick into the hole to try to close it. I get it closed. Second try, I get it open without an arc. The third one opens fine.

    OK, so now I know that these solid blade switches are not made to break a load and there is no means to put a load buster on them.

    I can't kill this whole circuit in the future because it feeds a couple of neighborhoods too.

    If I have to get these transformers off in the future, would you pull the elbows off of the bushings with a hot stick live? I've never done this or seen it done. What about re-energizing it? Would you only do it if you had access to the building to kill the load on the secondaries? I know if the elbows have white bands they are load break elbows, but I have no training on practical methods involving UG and pad mounts, any tips would be greatly appreciated.

    Maybe the best thing would be to change out the chocolate boxes to some decent switches, but in the meantime, I'm stuck with what is there.

  2. #2

    Default

    We break load with load break elbows all the time and I wouldn't hesitate going that route knowing what you do about the non load break switches, but rather than set up at 3 different pad mount transformers each time I believe I would push hard to change out the switches at the dip pole. One final thought, are the padmounts feed-thru type? if so do they have an internal switch?

  3. #3
    Join Date
    Mar 2003
    Location
    Jersey
    Posts
    2,512
    Blog Entries
    1

    Default

    I wouldn't make or break three phase load with an elbow, number one its prohibited on our property, number two you have the feroresonance possibility. Sounds to me like your engineers need to find a spot to cut in switches with load break capability.
    "It is not the critic who counts:The credit belongs to the man who is actually in the arena" Teddy Roosevelt

  4. #4
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    I am on the same page as LNF I would pull the elbows and park them, then go back and change the switches out to new . Also like LNF said if the transformer has an internal switch use it first then open the switches then park your elbows for a visual open, but either way I would be getting rid of those old switches. Not likely feroresonance at that voltage.

  5. Default

    Quote Originally Posted by Lineman North Florida View Post
    We break load with load break elbows all the time and I wouldn't hesitate going that route knowing what you do about the non load break switches, but rather than set up at 3 different pad mount transformers each time I believe I would push hard to change out the switches at the dip pole. One final thought, are the padmounts feed-thru type? if so do they have an internal switch?
    Next time we do infrared scanning and have everything open for inspection I'm going to check for the internal switches. They are feed through, that I know. I'd be hesitant to pull an elbow on the first one, that would be pulling the load on all three transformers. Then, the second elbow would have a huge load on it as everything is single phasing now. I guess the best way to do it if I had no choice would be to work the end of the line forward to the dip pole. Thanks to everyone that had input. I'm going to try to get the switches changed out, but, unfortunately, I have little say in the matter.

  6. #6
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    Take an amp check first, they are good up to 200 amps. I would be telling them I will be changing them the next time it is out. As far as an internal switch you would be able to see it when you open the door.

  7. Default

    Quote Originally Posted by lewy View Post
    Take an amp check first, they are good up to 200 amps. I would be telling them I will be changing them the next time it is out. As far as an internal switch you would be able to see it when you open the door.
    I pulled an elbow kit off the shelf the other day and read all the nomenclature. If I recall, inside the pad mount there are slots for parking stands, I'm pretty sure we don't have these stands. They would be a separate piece that slides into the slot. Some of our transformers have the red bushing covers sitting in those slots if there is anything there at all.

    I have to look into this or I'll end up with three hot cables flopping around someday. All our other locations have a dip pole for every transformer, there's no other location with multiple transformers on one run. I've never had to pull an elbow. We just pull the cutouts at the pole. I replaced concentric neutral cables once and did the terminations myself but I just put the elbows on the transformer by hand before I heated it up. If I ever get the opportunity with a de-energized transformer, I'm going to grab a shotgun stick and practice pulling and installing elbows.

  8. #8
    Join Date
    Feb 2007
    Location
    Ontario Canada
    Posts
    1,284

    Default

    You have to have parking stands as well as caps that go on the live bushings. You should give the elbows a slight twist to the right to break the seal, if they have never been pulled before can be quite difficult. I was reluctant to give advise on pulling a live elbow online.

  9. #9

    Default

    Quote Originally Posted by in the bucket View Post
    I pulled an elbow kit off the shelf the other day and read all the nomenclature. If I recall, inside the pad mount there are slots for parking stands, I'm pretty sure we don't have these stands. They would be a separate piece that slides into the slot. Some of our transformers have the red bushing covers sitting in those slots if there is anything there at all.

    I have to look into this or I'll end up with three hot cables flopping around someday. All our other locations have a dip pole for every transformer, there's no other location with multiple transformers on one run. I've never had to pull an elbow. We just pull the cutouts at the pole. I replaced concentric neutral cables once and did the terminations myself but I just put the elbows on the transformer by hand before I heated it up. If I ever get the opportunity with a de-energized transformer, I'm going to grab a shotgun stick and practice pulling and installing elbows.
    A company has to furnish you a few basic things, parking stands and joy caps and proper training on how to pull a live elbow just to name a few, after seeing the spot that they have put you in I would change out the switches and nothing more. Good luck. Charlie.

  10. #10
    Join Date
    Dec 2010
    Location
    Ontario, Canada
    Posts
    1,012

    Default

    Featured Sponsorr

    Just tell the boss those old chocolate boxes are cracked , and need to be replaced before they fail, causing an outage!