Originally Posted by
mrgrowl791
We have a three phase tap (about 3-4 miles long), going to a couple of 277-480 pad mounts at the end. (several single phase taps pull off of it) It is protected by 3 single phase hydraulic ocrs. It seems that a tree fell against one of the outside phases, openning up that one ocr. Is it possible to re-energize this phase from the pad mounts at the end of the tap?
P S What happen to dbbrown? I learned a lot from this guy. Very knowledgable.
it would depend on what type of bank it is. iff its a y-y then it will not backfeed (unless theres a generator hooked up) because all transformer coils are grounded, but as soon as you throw in a delta, high or low side everything is hot. might not be full line voltage but it will still be hot because there is not a ground on all coils