  1. Default bank transformer connection

    Featured Sponsor

    Good morning to all

    I have a question and I hope everyone involved in the answer

    When connecting the transformer bank is connected to only one of the transformers in the ground as shown in the picture
    Why

    And if there are any references Please advise us of

    I thank mybrother Pootnaigle
    for his answer, but I want more details


  2. #2
    Join Date
    Aug 2002
    Location
    Buffalo
    Posts
    3,000

    Default

    If you tried to put a ground on that transformer on the right on X2, your high side fuse would blow imediatly!

    Alot of linemen have dificulty with delta primary and secondaries. I've worked with them my whole carreer so it kinda comes easy for me. The thing to remember with a delta.... is that a delta can take one ground. It dosen't matter where the ground is as long as only one ground exists. That ground on X2, thats on the transformer to the left, mearly helps to give the bank secondary a refrence to ground and help the fuses clear in case of a fault on the secondary side.
    Last edited by topgroove; 07-09-2011 at 08:00 AM.

  3. #3
    Join Date
    Feb 2007
    Location
    Hartford, South Dakota
    Posts
    2,413

    Default

    Quote Originally Posted by saudi_lineman View Post
    Good morning to all

    I have a question and I hope everyone involved in the answer

    When connecting the transformer bank is connected to only one of the transformers in the ground as shown in the picture
    Why

    And if there are any references Please advise us of

    I thank mybrother Pootnaigle
    for his answer, but I want more details







    Saudi-Lineman….welcome! There is a man that frequents this forum, who spent over twenty years working on your system. We’ll see if he can answer your question!!!

  4. #4
    Join Date
    Aug 2002
    Location
    Buffalo
    Posts
    3,000

    Default

    thanks HD...... .... Damn you! I just blew half a beer out my nose laughing.

  5. #5
    Join Date
    Feb 2009
    Location
    Wisconsin
    Posts
    1,343

    Default

    Like TG said in an earlier post, that ground is there for refrance. I haven't seen one like this where the x2 is the ground, but I have built them with one of the x1 or x3 legs grounded. Usually b phase. On any system there can be one ground added intentionally or by accident, it's the secomd ground that will blow fuses, burn down wire and cause havoc. That first ground is to protect the system from unwanted current flow by being a direct short when the second ground appears.

  6. #6
    Join Date
    Aug 2002
    Location
    Buffalo
    Posts
    3,000

    Default

    I hear ya T-man. that is an intresting place to ground. We normaly ground the outside ,outside leg. We always use three transformers in a bank.

  7. Default

    Quote Originally Posted by topgroove View Post
    If you tried to put a ground on that transformer on the right on X2, your high side fuse would blow imediatly!

    Alot of linemen have dificulty with delta primary and secondaries. I've worked with them my whole carreer so it kinda comes easy for me. The thing to remember with a delta.... is that a delta can take one ground. It dosen't matter where the ground is as long as only one ground exists. That ground on X2, thats on the transformer to the left, mearly helps to give the bank secondary a refrence to ground and help the fuses clear in case of a fault on the secondary side.

    Quote Originally Posted by Highplains Drifter View Post
    Saudi-Lineman….welcome! There is a man that frequents this forum, who spent over twenty years working on your system. We’ll see if he can answer your question!!!
    pls try to found him and ask about this

    Quote Originally Posted by T-Man View Post
    Like TG said in an earlier post, that ground is there for refrance. I haven't seen one like this where the x2 is the ground, but I have built them with one of the x1 or x3 legs grounded. Usually b phase. On any system there can be one ground added intentionally or by accident, it's the secomd ground that will blow fuses, burn down wire and cause havoc. That first ground is to protect the system from unwanted current flow by being a direct short when the second ground appears.

    i know the fueses will burn but if we connect all transforme to the ground x2 why fuses burn this is what i mean
    if you say short circut tell me how?

    thanks guyz

  8. #8
    Join Date
    Aug 2002
    Location
    Buffalo
    Posts
    3,000

    Default

    You saudi guys crack me up... Always trying to blow stuff up. The reason the fuse will blow is by grounding that second transfotmer your putting a second ground on a oppisite leg. Your confusing a wye with a delta. With a delta there is no common.

  9. #9

    Default

    [/quote=saudi_lineman;108412]
    [/quote]

    I'm surprised that Groove & T-Man have never seen this hookup. I've built thousands of these OD banks, 120v, 240v, 208v. They are used for many applications. A residence with a 2 or 3 wire service with a 4 wire 3 phase well service. Commercial building with an office and 3 phase motor load. Small horsepower water wells. We wire the secondary delta a little different, but the outcome is the same.

    If you tried to put a ground on that transformer on the right on X2, your high side fuse would blow imediatly!
    Alot of linemen have dificulty with delta primary and secondaries. I've worked with them my whole carreer so it kinda comes easy for me. The thing to remember with a delta.... is that a delta can take one ground. It dosen't matter where the ground is as long as only one ground exists. That ground on X2, thats on the transformer to the left, mearly helps to give the bank secondary a refrence to ground and help the fuses clear in case of a fault on the secondary side.
    Groove, I'm not sure what you've said is true, I may be wrong. The ground on X2 to the left, gives a voltage reference to the bank. If you vector it out (haven't done that in over 30yrs) you can measure 120, 240, & 208. What that diagram doesn't show is C phase to X2, which is 208v.
    Here's a pic I took this morn. of a 240v 3 wire bank........

    Name:  OD 002.jpg
Views: 8885
Size:  80.2 KB

    No neutral, all it's seeing is phase to phase.

    Here's how we wire these banks...

    Name:  OD 003.jpg
Views: 24764
Size:  71.7 KB

    The delta is different from the diagram, having the outside bushing of the right side TX being the stinger, or power leg, 208v to neutral.

    Here's a pic about a 1/2mi from my house, commercial on on side of the street, residential on the other. There are 3 OD banks almost in a row. The closest one shows service to 2 commercial cust., and to the right, 2 houses. On this 3/4mi street, I counted over 35 OD banks. It's versital, and cheaper than a closed bank.
    Just my thoughts.
    Attached Images Attached Images  

  10. #10
    Join Date
    Oct 2006
    Location
    South East Texas
    Posts
    3,278

    Default

    Featured Sponsorr

    Ummmmmmm we also built our 2 pot banks like this for 120-240-3 phase . Like Barehander said there is a hi leg. But all phase to phase secondary voltage is 240.
    If you look closely at his drawing the centertap( ground) could be removed since there is no neutral in his circuit, to carry a 120 volt return anyway. I beleive ONE ground can be applied anywhere regardless if its on A, B, or C phase or on the centertap itself. the second one is always gonna blow sumpin up.
    He isnt understanding that he is essentially making ONE transformer out of 2, or 3. and ONLY One ground can be applied on any Transformer.